I quote below, the full amendment to the Boiler Regs, as sent to me by the Southern Federation. Couldn't quite get the text layout right on here (I copied and pasted from Word!). However, I hope it will help you and others:
"Revision to Boiler Test Code With Regard to Small Boilers
Introduction. Page 3, paragraph 4. Delete existing paragraph and replace with:
Small boilers (i.e boilers with a capacity of not more than 3.0 bar-litres) are exempted from
The requirements of this code. However, it is recommended that small boilers be fitted
with, at least, a safety valve and a pressure gauge and that these be tested every 12 months
in order to ensure correct operation at the correct release pressure. The boiler and the
pipework installation should also be checked at least every 12 months.
And also:
Page 11, Section 10 Steam Test. Delete the whole section and replace with:
10. Steam Test
10.1 An examination under steam pressure shall be undertaken, a) before first placing the boiler into service, b) after every hydraulic test, and c) at intervals not exceeding fourteen months.
10.2 The boiler shall be steamed and further examinations carried out as pressure is rising and whilst the boiler is at working pressure.
10.3 Correct operation of the following items shall be verified:
· Boiler water feeding arrangements by at least two independent means (hand pump, injectors, mechanical pump. Etc.)
· Pressure gauge.
· The water gauge(s) should be blown down and the water should be seen to recover to its level without delay.
10.4 On boilers of less than 10 bar-litre capacity with a total internal volume not exceeding
Two (2) litres it is acknowledged that the provision of two independent means of water feed arrangement may not be possible. Therefore for the purpose of testing these boilers:
a) One (1) means of water feed arrangement is acceptable
b) Water in the gauge glass must recover its level without delay following movement of the boiler. Water gauges fitted to boats whose boilers fall within this size category do not have to be capable of being blown down.
c) The water gauge and pressure gauge should be clearly visible.
10.5 The boiler shall then be steamed at maximum firing rate and with full blower
operation. The test shall be continued for sufficient time as to allow the Inspector to
be satisfied that stable conditions have been attained. The operation of the safety
valves shall be checked to ensure that they operate at working pressure and that
pressure does not rise by more than 10% of the working pressure during safety valve
operation."